Electrical EngineeringHard
A wattmeter is connected through a 400/5 A CT and a 3300/110 V PT. It reads 500 W. The actual power in the primary circuit is
- A. 55 kW
- B. 15 kW
- C. 1200 kW
- D. 40 kW
Correct answer: C. 1200 kW
P = W × CT ratio × PT ratio = 500×80×30 W = 1200.00 kW.
Practise more Circuits, Networks & Electrical Measurements (Electrical) questionsCircuits, Networks & Electrical Measurements (Electrical): notes and key points