Electrical EngineeringHard
A balanced 3-phase load of 30 kW at 0.7 lagging pf is fed from a 400 V line supply. The line current is
- A. 61.86 A
- B. 35.71 A
- C. 43.3 A
- D. 107.14 A
Correct answer: A. 61.86 A
I = P/(√3 VL cosφ) = 61.86 A. (Standard formula applied.)