Electrical EngineeringVery hard
A single-phase 230 V, 60 Hz motor load takes 5 kW at 0.75 lagging. The shunt capacitance needed to bring pf to unity is
- A. 250.7 µF
- B. 442.2 µF
- C. 221.1 µF
- D. 50855.6 µF
Correct answer: C. 221.1 µF
Qc = P tanφ = 4410 var; C = Qc/(ωV²) = 221.1 µF.
Practise more Circuits, Networks & Electrical Measurements (Electrical) questionsCircuits, Networks & Electrical Measurements (Electrical): notes and key points
More Circuits, Networks & Electrical Measurements (Electrical) questions
- A coil of 10 Ω resistance and 1 H inductance is connected to a 24 V dc supply at t = 0. The current at t = 50.0 ms is
- A coil of 25 Ω resistance and 2 H inductance is connected to a 100 V dc supply at t = 0. The current at t = 80.0 ms is
- A series R-L circuit (R = 5 Ω, L = 0.5 H) is switched on to a dc source. The time taken for the current to reach 99% of its final value is
- A 10 µF capacitor charged to 50 V discharges through a 220 kΩ resistor. The time for its voltage to fall to 10 V is
- An uncharged 50 µF capacitor is connected through 10 kΩ to a 50 V dc source. At t = 1.000 s the capacitor voltage is
- Two coupled coils have L1 = 1 H, L2 = 0.5 H and coupling coefficient k = 0.6. Connected in series opposing, the total inductance is