Electrical EngineeringVery hard
A hall of area 50 m² needs an average illuminance of 200 lux. The utilisation factor is 0.55 and the maintenance factor is 0.75. The total lumens required from the lamps is
- A. 13636 lm
- B. 4125 lm
- C. 18182 lm
- D. 24242 lm
Correct answer: D. 24242 lm
Φ = EA/(UF × MF) = 200×50/(0.55×0.75) = 24242 lm.