Electrical EngineeringVery hard
An inverter of 200 W load must run for 4 h from a 48 V battery bank. With a permitted depth of discharge of 50% and inverter efficiency 85%, the minimum battery capacity is
- A. 39.2 Ah
- B. 19.6 Ah
- C. 33.3 Ah
- D. 16.7 Ah
Correct answer: A. 39.2 Ah
Ah = P t/(V × DoD × η) = 200×4/(48×0.5×0.85) = 39.2 Ah.