Electrical EngineeringVery hard
A star-connected synchronous generator (resistance neglected, Xs = 4 Ω per phase) has an open-circuit line emf 17940 V and is connected to an infinite bus of 13800 V (line). At a power angle of 40° the power delivered is
- A. 13.261 MW
- B. 39.784 MW
- C. 119.352 MW
- D. 68.908 MW
Correct answer: B. 39.784 MW
P = 3(EV/Xs) sinδ with phase values E = 10358 V, V = 7967 V = 39.784 MW.