Electrical EngineeringVery hard
A 100 kVA distribution transformer (iron loss 500 W, full-load copper loss 300 W) supplies unity-pf load of 1 of full load for 4 h and 0.5 of full load for 8 h, and is on no load for the rest of the 24 h. Its all-day efficiency is
- A. 97.48 %
- B. 98.23 %
- C. 98.3 %
- D. 99.03 %
Correct answer: C. 98.3 %
Output = 800 kWh; core loss = 500×24/1000 = 12 kWh; copper = 1.8 kWh; η = 98.30 %.