Electrical EngineeringVery hard

Using Peek's formula with air density factor 1, a 3-phase line has conductor radius 0.8 cm, spacing 300 cm and surface irregularity factor 0.85. The disruptive critical line voltage (rms, line-to-line) is (take g0 = 21.1 kV/cm)

  1. A. 255.1 kV
  2. B. 85 kV
  3. C. 147.3 kV
  4. D. 64 kV

Correct answer: C. 147.3 kV

Vc(phase) = 21.1 m δ r ln(d/r) = 85.04 kV; line = √3 Vc = 147.3 kV.