A room's cooling load has 20 kW sensible and 8 kW latent components. The sensible heat factor is
- A. 0.286
- B. 2.500
- C. 0.643
- D. 0.714
Correct answer: D. 0.714
SHF = SH/(SH + LH) = 20/28 = 0.714.