Mechanical EngineeringVery hard
A counter-flow exchanger transfers 200 kW with hot fluid cooling 120 → 80 °C and cold fluid heating 20 → 50 °C. With U = 500 W/m²·K, the required area is
- A. 4.93 m²
- B. 7.71 m²
- C. 6.17 m²
- D. 6.88 m²
Correct answer: C. 6.17 m²
ΔT1 = 70, ΔT2 = 60; LMTD = 64.87 °C; A = Q/(U·LMTD) = 200000/(500×64.87) = 6.17 m².