Two loads are connected in parallel to one AC supply: load 1 takes 3 kW at power factor 0.6 lagging, load 2 takes 4 kW at power factor 0.8 leading. The power factor of the combination is
- A. 0.990 leading
- B. 0.700 lagging
- C. 1.000
- D. 0.990 lagging
Correct answer: D. 0.990 lagging
Reactive powers: load 1 draws 4 kVAR (lagging), load 2 supplies 3 kVAR (leading). Net P = 7 kW, Q = 1 kVAR lagging, S = √50 = 7.07 kVA, so cos φ = 0.990 lagging. Adding apparent powers (5 + 5) is the trap.