Electrical EngineeringVery hard
In the two-wattmeter method on a balanced 3-phase load the readings are 6000 W and 1500 W (both positive). The load power factor is
- A. 0.722
- B. 0.25
- C. 0.693
- D. 0.857
Correct answer: C. 0.693
tanφ = √3(W1-W2)/(W1+W2) = 1.039; pf = cosφ = 0.693.