Electrical EngineeringVery hard
Two single-phase transformers (X/R ratios equal) of 300 kVA, 5% impedance and 100 kVA, 4% impedance operate in parallel and share a total load of 400 kVA. The load carried by the 300 kVA unit is
- A. 300 kVA
- B. 117.6 kVA
- C. 222.2 kVA
- D. 282.4 kVA
Correct answer: D. 282.4 kVA
Share ∝ kVA/%Z: 60.00 and 25.00; S1 = 400×60.00/85.00 = 282.4 kVA.
Practise more Electrical Machines (Electrical) questionsElectrical Machines (Electrical): notes and key points