Electrical EngineeringVery hard
A 3-unit insulator string has shunt-to-self capacitance ratio 0.25 and 110 kV across the whole string. The voltage across the unit nearest the line conductor is
- A. 49.08 kV
- B. 33.85 kV
- C. 27.08 kV
- D. 36.67 kV
Correct answer: A. 49.08 kV
V1 = 27.08 kV (top unit); V3 = V1(1+3k+k²) = 49.08 kV.