Electrical EngineeringHard
A 3-phase transmission line has conductors of radius 1.5 cm arranged at the corners of an equilateral triangle of side 6 m (solid conductors, ignore transposition effects). The inductance per phase per km is
- A. 1.1983 mH/km
- B. 0.6241 mH/km
- C. 2.4966 mH/km
- D. 1.2483 mH/km
Correct answer: D. 1.2483 mH/km
L = 0.2 ln(D/r') mH/km, r' = 0.7788r = 1.168 cm: L = 1.2483 mH/km.