Electrical EngineeringHard
A 3-phase transmission line has conductors of radius 1 cm arranged at the corners of an equilateral triangle of side 8 m (solid conductors, ignore transposition effects). The inductance per phase per km is
- A. 2.7738 mH/km
- B. 1.3869 mH/km
- C. 0.6935 mH/km
- D. 1.3369 mH/km
Correct answer: B. 1.3869 mH/km
L = 0.2 ln(D/r') mH/km, r' = 0.7788r = 0.779 cm: L = 1.3869 mH/km.
Practise more Power Systems & Protection (Electrical) questionsPower Systems & Protection (Electrical): notes and key points
More Power Systems & Protection (Electrical) questions
- A 3-phase transmission line has conductors of radius 0.8 cm arranged at the corners of an equilateral triangle of side 6 m (solid…
- A 3-phase line has conductors of radius 1.2 cm at the corners of an equilateral triangle of side 8 m. The capacitance to neutral per phase…
- Using Peek's formula with air density factor 1, a 3-phase line has conductor radius 1.5 cm, spacing 250 cm and surface irregularity factor…
- Using Peek's formula with air density factor 1, a 3-phase line has conductor radius 0.8 cm, spacing 300 cm and surface irregularity factor…
- A 3-bus system has lines 1-2 (reactance 0.4 pu) and 1-3 (reactance 0.1 pu), no shunt elements. The diagonal element Y11 of the bus…
- A hydroelectric station has a net head of 100 m and a discharge of 50 m³/s. With an overall efficiency of 90%, the electrical power output…