Using Peek's formula with air density factor 1, a 3-phase line has conductor radius 1.5 cm, spacing 250 cm and surface irregularity factor 1. The disruptive critical line voltage (rms, line-to-line) is (take g0 = 21.1 kV/cm)

  1. A. 485.8 kV
  2. B. 161.9 kV
  3. C. 121.8 kV
  4. D. 280.5 kV

Correct answer: D. 280.5 kV

Vc(phase) = 21.1 m δ r ln(d/r) = 161.92 kV; line = √3 Vc = 280.5 kV.