Electrical EngineeringVery hard
Using Peek's formula with air density factor 1, a 3-phase line has conductor radius 1.5 cm, spacing 250 cm and surface irregularity factor 1. The disruptive critical line voltage (rms, line-to-line) is (take g0 = 21.1 kV/cm)
- A. 485.8 kV
- B. 161.9 kV
- C. 121.8 kV
- D. 280.5 kV
Correct answer: D. 280.5 kV
Vc(phase) = 21.1 m δ r ln(d/r) = 161.92 kV; line = √3 Vc = 280.5 kV.