Electrical EngineeringHard
A 3-phase line has conductors of radius 1.2 cm at the corners of an equilateral triangle of side 8 m. The capacitance to neutral per phase per km is (ε0 = 8.854 pF/m)
- A. 0.00824 µF/km
- B. 0.01711 µF/km
- C. 0.00856 µF/km
- D. 0.00428 µF/km
Correct answer: C. 0.00856 µF/km
C = 2πε0/ln(D/r) = 0.00856 µF/km. (Standard formula applied.)