Electrical EngineeringHard
A single-core cable must withstand a peak voltage of 100 kV to the sheath of internal radius 4 cm. With the conductor radius chosen for minimum stress at the surface, that minimum maximum-stress is
- A. 9.2 kV/cm
- B. 67.96 kV/cm
- C. 25 kV/cm
- D. 50 kV/cm
Correct answer: B. 67.96 kV/cm
Optimum r = R/e = 1.472 cm; gmin = eV/R = 67.96 kV/cm.