Mechanical EngineeringHard
A room's cooling load has 30 kW sensible and 15 kW latent components. The sensible heat factor is
- A. 2.000
- B. 0.833
- C. 0.667
- D. 0.333
Correct answer: C. 0.667
SHF = SH/(SH + LH) = 30/45 = 0.667.
Practise more Heat Transfer, Refrigeration & Air Conditioning (Mechanical) questionsHeat Transfer, Refrigeration & Air Conditioning (Mechanical): notes and key points
More Heat Transfer, Refrigeration & Air Conditioning (Mechanical) questions
- A room's cooling load has 20 kW sensible and 8 kW latent components. The sensible heat factor is
- Air at 28 °C DBT passes through a cooling coil with an apparatus dew point of 8 °C and a bypass factor of 0.2. The DBT of air leaving the…
- Air at 35 °C DBT passes through a cooling coil with an apparatus dew point of 10 °C and a bypass factor of 0.4. The DBT of air leaving the…
- A fluid has dynamic viscosity 0.2 Pa·s, specific heat 1900 J/kg·K and thermal conductivity 0.145 W/m·K. Its Prandtl number is
- A fluid has dynamic viscosity 0.00002 Pa·s, specific heat 1008 J/kg·K and thermal conductivity 0.029 W/m·K. Its Prandtl number is
- A solid with k = 200 W/m·K, ρ = 7800 kg/m³ and c = 900 J/kg·K has a characteristic length of 50 mm. The Fourier number after 300 s is