Mechanical EngineeringHard
In a counter-flow heat exchanger the hot fluid cools from 180 °C to 80 °C while the cold fluid heats from 20 °C to 50 °C. The LMTD is
- A. 95.0 °C
- B. 77.7 °C
- C. 90.5 °C
- D. 97.1 °C
Correct answer: C. 90.5 °C
ΔT1 = 130, ΔT2 = 60; LMTD = (ΔT1 − ΔT2)/ln(ΔT1/ΔT2) = 90.5 °C.
Practise more Heat Transfer, Refrigeration & Air Conditioning (Mechanical) questionsHeat Transfer, Refrigeration & Air Conditioning (Mechanical): notes and key points
More Heat Transfer, Refrigeration & Air Conditioning (Mechanical) questions
- A counter-flow exchanger transfers 200 kW with hot fluid cooling 120 → 80 °C and cold fluid heating 20 → 50 °C. With U = 500 W/m²·K, the…
- A counter-flow heat exchanger has Cmin = 1000 W/K, a capacity ratio Cr = 0.75 and UA = 2000 W/K. Its effectiveness is
- Hot water (1.5 kg/s, 80 °C) and cold water (1 kg/s, 25 °C) flow in a counter-flow exchanger with UA = 1000 W/K (c = 4180 J/kg·K). The heat…
- A plane tube wall of 2 mm thickness (k = 50 W/m·K) separates fluids with h = 2000 W/m²·K inside and 100 W/m²·K outside. The overall heat…
- A wall 150 mm thick (k = 0.7 W/m·K) has still indoor air at 25 °C (h = 12 W/m²·K) on one side and outdoor air at -5 °C (h = 20 W/m²·K) on…
- A small grey body (ε = 0.9, area 2 m²) at 200 °C sits in a large enclosure whose walls are at 25 °C. The net radiant heat loss is