Electrical EngineeringHard
A balanced 3-phase load of 75 kW at 0.75 lagging pf is fed from a 400 V line supply. The line current is
- A. 250 A
- B. 83.33 A
- C. 108.25 A
- D. 144.34 A
Correct answer: D. 144.34 A
I = P/(√3 VL cosφ) = 144.34 A.