A 3-phase star-star transformer is rated 6600/400 V (line voltages). The ratio of primary to secondary turns per phase is
- A. 16.5
- B. 28.58
- C. 5.5
- D. 49.5
Correct answer: A. 16.5
Phase voltage ratio = (V1ph)/(V2ph) = 16.50 for star-star connection.