Electrical EngineeringVery hard
A medium transmission line (nominal-π, resistance neglected) has total series reactance 100 Ω and total shunt susceptance 1000 µS. With 132 kV (line) at the sending end and the receiving end open, the receiving-end voltage is
- A. 135.38 kV
- B. 125.4 kV
- C. 146.67 kV
- D. 138.95 kV
Correct answer: D. 138.95 kV
A = 1 + YZ/2 = 1 - XB/2 = 0.9500; Vr(no load) = Vs/A = 138.95 kV (Ferranti rise).
Practise more Power Systems & Protection (Electrical) questionsPower Systems & Protection (Electrical): notes and key points