Electrical EngineeringVery hard
For a nominal-π line with series impedance j100 Ω and total shunt admittance j500 µS, the ABCD constant C has magnitude
- A. 506.25 µS
- B. 493.75 µS
- C. 487.5 µS
- D. 500 µS
Correct answer: B. 493.75 µS
C = Y(1 + YZ/4) = jB(1 - XB/4) = 493.75 µS. (Standard formula applied.)