Electrical EngineeringHard
A 50 MVA, 6.6 kV generator with subtransient reactance 0.25 pu has a 3-phase fault at its terminals (prefault voltage 1 pu, no load). The initial symmetrical fault current is
- A. 10101 A
- B. 17495 A
- C. 30303 A
- D. 4374 A
Correct answer: B. 17495 A
Fault MVA = S/X'' = 200.0 MVA; I = MVA/(√3 kV) = 17495 A.