Electrical EngineeringVery hard
For a double line-to-ground fault at a bus with X1 = 0.2, X2 = 0.15, X0 = 0.4 pu (prefault 1 pu, solid fault), the current flowing into the ground is
- A. 3.235 pu
- B. 2.647 pu
- C. 9.706 pu
- D. 4 pu
Correct answer: B. 2.647 pu
Ia1 = 1/(X1 + X2||X0) = 3.235; Ia0 = Ia1·X2/(X2+X0) = 0.882; Ig = 3Ia0 = 2.647 pu.