The symmetrical short-circuit level at a 11 kV bus is 500 MVA. The symmetrical breaking current rating needed for a circuit breaker there is
- A. 78.73 kA
- B. 45.45 kA
- C. 26.24 kA
- D. 15.15 kA
Correct answer: C. 26.24 kA
I = MVA/(√3 kV) = 26.24 kA. (Standard formula applied.)