A relay (5 A rating) with plug setting 100% is fed by a 600/5 A CT. For a primary fault current of 6000 A, the plug-setting multiplier is
- A. 10
- B. 8
- C. 50
- D. 12.5
Correct answer: A. 10
Secondary current = 6000×5/600 = 50.00 A; pick-up = 5 A; PSM = 10.00.