Electrical EngineeringHard
A consumer's load is 1000 kW at 0.75 lagging. After installing a capacitor bank to improve the pf to 0.95 lagging, the reduction in kVA demand is
- A. 266.7 kVA
- B. 553.2 kVA
- C. 200 kVA
- D. 280.7 kVA
Correct answer: D. 280.7 kVA
kVA1 = 1000/0.75 = 1333.3; kVA2 = 1000/0.95 = 1052.6; reduction = 280.7 kVA (capacitor kVAR = 553.2).