A consumer's load is 1000 kW at 0.75 lagging. After installing a capacitor bank to improve the pf to 0.95 lagging, the reduction in kVA demand is

  1. A. 266.7 kVA
  2. B. 553.2 kVA
  3. C. 200 kVA
  4. D. 280.7 kVA

Correct answer: D. 280.7 kVA

kVA1 = 1000/0.75 = 1333.3; kVA2 = 1000/0.95 = 1052.6; reduction = 280.7 kVA (capacitor kVAR = 553.2).