Electrical EngineeringVery hard
A single-core cable has conductor radius 1 cm, sheath internal radius 1.5 cm and insulation of relative permittivity 3. For a 10 km length of a 3-phase 11 kV, 50 Hz system, the charging current per phase is
- A. 14.22 A
- B. 24.64 A
- C. 4.74 A
- D. 8.21 A
Correct answer: D. 8.21 A
C = 2πε0εr l/ln(R/r) = 4.116 µF; Ic = ωC Vph = 8.21 A.
Practise more Power Systems & Protection (Electrical) questionsPower Systems & Protection (Electrical): notes and key points