Electrical EngineeringVery hard
A single-core cable for a 11 kV (line) 3-phase system has conductor radius 1.5 cm and sheath radius 3 cm. The maximum electric stress in the dielectric (peak) is
- A. 5.99 kV/cm
- B. 8.64 kV/cm
- C. 4.32 kV/cm
- D. 10.58 kV/cm
Correct answer: B. 8.64 kV/cm
Vpeak(phase) = 11√2/√3 = 8.98 kV; gmax = V/(r ln(R/r)) = 8.64 kV/cm.