Electrical EngineeringVery hard

A generator delivering Pm = 0.3 of its maximum power transfer capacity Pmax (pre-fault) suffers a 3-phase fault at its terminals (so Pe = 0 during the fault), cleared with the post-fault network equal to the pre-fault network. By the equal-area criterion the critical clearing angle is

  1. A. 162.5 °
  2. B. 17.5 °
  3. C. 40.6 °
  4. D. 101.2 °

Correct answer: D. 101.2 °

δ0 = sin⁻¹(0.3) = 17.46°; δmax = 180° - δ0; cosδcr = (Pm/Pmax)(δmax - δ0) + cosδmax = -0.1943; δcr = 101.2°.