For a double line-to-ground fault at a bus with X1 = 0.1, X2 = 0.15, X0 = 0.05 pu (prefault 1 pu, solid fault), the current flowing into the ground is
- A. 21.818 pu
- B. 10 pu
- C. 7.273 pu
- D. 16.364 pu
Correct answer: D. 16.364 pu
Ia1 = 1/(X1 + X2||X0) = 7.273; Ia0 = Ia1·X2/(X2+X0) = 5.455; Ig = 3Ia0 = 16.364 pu.