Electrical EngineeringVery hard

For a double line-to-ground fault at a bus with X1 = 0.1, X2 = 0.15, X0 = 0.05 pu (prefault 1 pu, solid fault), the current flowing into the ground is

  1. A. 21.818 pu
  2. B. 10 pu
  3. C. 7.273 pu
  4. D. 16.364 pu

Correct answer: D. 16.364 pu

Ia1 = 1/(X1 + X2||X0) = 7.273; Ia0 = Ia1·X2/(X2+X0) = 5.455; Ig = 3Ia0 = 16.364 pu.