Electrical EngineeringVery hard
On a 50 MVA, 11 kV base, the sequence reactances at a bus are X1 = 0.1, X2 = 0.2, X0 = 0.1 pu. For a solid single line-to-ground fault (prefault 1 pu) the fault current is
- A. 19682 A
- B. 26243 A
- C. 13122 A
- D. 6561 A
Correct answer: A. 19682 A
If = 3E/(Z1+Z2+Z0) = 7.500 pu; Ibase = 2624.3 A; If = 19682 A.
Practise more Power Systems & Protection (Electrical) questionsPower Systems & Protection (Electrical): notes and key points
More Power Systems & Protection (Electrical) questions
- On a 100 MVA, 33 kV base, X1 = 0.25 pu and X2 = 0.2 pu at a bus. For a bolted line-to-line fault (prefault 1 pu), the magnitude of the…
- For a double line-to-ground fault at a bus with X1 = 0.2, X2 = 0.15, X0 = 0.4 pu (prefault 1 pu, solid fault), the current flowing into…
- For a double line-to-ground fault at a bus with X1 = 0.1, X2 = 0.15, X0 = 0.05 pu (prefault 1 pu, solid fault), the current flowing into…
- The symmetrical short-circuit level at a 11 kV bus is 500 MVA. The symmetrical breaking current rating needed for a circuit breaker there is
- A relay (5 A rating) with plug setting 100% is fed by a 600/5 A CT. For a primary fault current of 6000 A, the plug-setting multiplier is
- A plant has a maximum demand of 80 MW and supplies 385440 MWh in a year of 8760 h. Its load factor is