Electrical EngineeringVery hard
On a 100 MVA, 33 kV base, X1 = 0.25 pu and X2 = 0.2 pu at a bus. For a bolted line-to-line fault (prefault 1 pu), the magnitude of the fault current in the faulted phases is
- A. 11664 A
- B. 6734 A
- C. 8942 A
- D. 3888 A
Correct answer: B. 6734 A
Ib(fault) = √3 E/(Z1+Z2) = 3.849 pu; × 1749.5 A = 6734 A.