Electrical EngineeringVery hard

On a 50 MVA, 132 kV base, the sequence reactances at a bus are X1 = 0.1, X2 = 0.1, X0 = 0.3 pu. For a solid single line-to-ground fault (prefault 1 pu) the fault current is

  1. A. 875 A
  2. B. 2187 A
  3. C. 437 A
  4. D. 1312 A

Correct answer: D. 1312 A

If = 3E/(Z1+Z2+Z0) = 6.000 pu; Ibase = 218.7 A; If = 1312 A.