Electrical EngineeringVery hard
A generator has a reactance of 0.25 pu on its own rating of 50 MVA, 33 kV. Its reactance on a base of 250 MVA, 31.35 kV is
- A. 1.25 pu
- B. 0.0554 pu
- C. 1.385 pu
- D. 1.1281 pu
Correct answer: C. 1.385 pu
Znew = Zold (Snew/Sold)(Vold/Vnew)² = 0.25×5×1.1080 = 1.3850 pu.