Electrical EngineeringHard
A transmission line has a reactance of 8 Ω. Its per-unit value on a base of 200 MVA and 66 kV (line-to-line) is
- A. 0.3673 pu
- B. 0.1224 pu
- C. 0.2121 pu
- D. 174.24 pu
Correct answer: A. 0.3673 pu
Zbase = kV²/MVA = 21.780 Ω; pu = 8/21.780 = 0.3673.
Practise more Power Systems & Protection (Electrical) questionsPower Systems & Protection (Electrical): notes and key points
More Power Systems & Protection (Electrical) questions
- A 50 MVA, 6.6 kV generator with subtransient reactance 0.25 pu has a 3-phase fault at its terminals (prefault voltage 1 pu, no load). The…
- On a 50 MVA, 132 kV base, the sequence reactances at a bus are X1 = 0.1, X2 = 0.1, X0 = 0.3 pu. For a solid single line-to-ground fault…
- On a 50 MVA, 11 kV base, the sequence reactances at a bus are X1 = 0.1, X2 = 0.2, X0 = 0.1 pu. For a solid single line-to-ground fault…
- On a 100 MVA, 33 kV base, X1 = 0.25 pu and X2 = 0.2 pu at a bus. For a bolted line-to-line fault (prefault 1 pu), the magnitude of the…
- For a double line-to-ground fault at a bus with X1 = 0.2, X2 = 0.15, X0 = 0.4 pu (prefault 1 pu, solid fault), the current flowing into…
- For a double line-to-ground fault at a bus with X1 = 0.1, X2 = 0.15, X0 = 0.05 pu (prefault 1 pu, solid fault), the current flowing into…