Mechanical EngineeringVery hard
A plant makes 15 tonnes of ice per day from water at 30 °C, the ice leaving at −5 °C (cpw = 4.18, latent heat 335 kJ/kg, cp,ice = 2.1 kJ/kg·K). Taking 1 TR = 3.517 kW, the refrigeration capacity is
- A. 81.8 TR
- B. 16.5 TR
- C. 23.2 TR
- D. 21.1 TR
Correct answer: C. 23.2 TR
Q = m(cpwT + 335 + cp,iceTi) = 7063500 kJ/day = 81.75 kW; TR = 81.75/3.517 = 23.2.