Electrical EngineeringHard
A balanced star-connected load with 15 + j9 Ω per phase is supplied from a 440 V line-to-line, 3-phase source. The total active power is
- A. 3.163 kW
- B. 5.479 kW
- C. 28.471 kW
- D. 9.49 kW
Correct answer: D. 9.49 kW
Vph = 254.0 V; Iph = Vph/|Z|; P = 3Iph²R = VL²R/|Z|² = 9.490 kW.
Practise more Circuits, Networks & Electrical Measurements (Electrical) questionsCircuits, Networks & Electrical Measurements (Electrical): notes and key points
More Circuits, Networks & Electrical Measurements (Electrical) questions
- Three identical resistors draw 3 kW when connected in star across a 440 V, 3-phase supply. When the same three resistors are reconnected…
- A balanced 3-phase load of 75 kW at 0.75 lagging pf is fed from a 400 V line supply. The line current is
- In the two-wattmeter method on a balanced 3-phase load the readings are 2000 W and 1000 W (both positive). The load power factor is
- In the two-wattmeter method on a balanced 3-phase load the readings are 3000 W and 2500 W (both positive). The load power factor is
- In the two-wattmeter method on a balanced 3-phase load the readings are 6000 W and 1500 W (both positive). The load power factor is
- A load of 80 kW operates at 0.6 lagging pf. The capacitor kVAR required to raise the pf to 1 is