Electrical EngineeringHard
Three identical resistors draw 3 kW when connected in star across a 440 V, 3-phase supply. When the same three resistors are reconnected in delta across the same supply, they draw
- A. 1 kW
- B. 3 kW
- C. 9 kW
- D. 5.2 kW
Correct answer: C. 9 kW
Phase voltage rises by √3, so phase power ×3: 9 kW.