Electrical EngineeringVery hard
A 8 kVA load is supplied at 300 V from a 600 V single-phase supply through an ideal auto-transformer. The kVA transferred magnetically (transformed) is
- A. 4 kVA
- B. 6 kVA
- C. 8 kVA
- D. 5 kVA
Correct answer: A. 4 kVA
k = V2/V1 = 0.5000; transformed power = S(1 - k) = 4.000 kVA; the rest is conducted directly.