Electrical EngineeringVery hard
A short 3-phase line (total R = 1.63 Ω, X = 5.45 Ω per phase) delivers 20 MW at 33 kV (line) and 0.85 pf lagging. The percentage voltage regulation is
- A. 15.3 %
- B. 16.46 %
- C. 9.5 %
- D. -2.49 %
Correct answer: C. 9.5 %
I = P/(√3 V cosφ) = 411.7 A; Vs = |Vr + I(R cosφ + X sinφ) + jI(X cosφ - R sinφ)| = 20.863 kV (phase); Reg = 9.50 %.