Electrical EngineeringHard
A transmission line loses 6 MW when delivering a fixed load at unity pf at 66 kV. If the transmission voltage is raised to 132 kV for the same power and same conductor, the line loss becomes
- A. 12 MW
- B. 1.5 MW
- C. 3 MW
- D. 0.75 MW
Correct answer: B. 1.5 MW
Loss = 3I²R and I ∝ 1/V, so loss ∝ 1/V²: 6/4 = 1.500 MW.