Mechanical EngineeringHard
An ideal reversed Brayton (Bell–Coleman) air refrigerator operates at a pressure ratio of 4 with γ = 1.4. Its COP is
- A. 2.06
- B. 1.35
- C. 0.49
- D. 2.57
Correct answer: A. 2.06
COP = 1/(rp^((γ−1)/γ) − 1) = 1/(1.4860 − 1) = 2.06.