Mechanical EngineeringVery hard
In a Bell–Coleman cycle air leaves the cold space at -10 °C and, after compression to a pressure ratio of 5 and cooling, enters the expander at 20 °C. With γ = 1.4 and cp = 1.005 kJ/kg·K, the refrigerating effect per kg is
- A. 98.0 kJ/kg
- B. 205.4 kJ/kg
- C. 62.7 kJ/kg
- D. 78.4 kJ/kg
Correct answer: D. 78.4 kJ/kg
T4 = T3/rp^0.2857 = 185.0 K; RE = cp(T1 − T4) = 1.005×(263 − 185.0) = 78.4 kJ/kg.
Practise more Heat Transfer, Refrigeration & Air Conditioning (Mechanical) questionsHeat Transfer, Refrigeration & Air Conditioning (Mechanical): notes and key points
More Heat Transfer, Refrigeration & Air Conditioning (Mechanical) questions
- A plant makes 10 tonnes of ice per day from water at 30 °C, the ice leaving at −8 °C (cpw = 4.18, latent heat 335 kJ/kg, cp,ice = 2.1…
- A plant makes 15 tonnes of ice per day from water at 30 °C, the ice leaving at −5 °C (cpw = 4.18, latent heat 335 kJ/kg, cp,ice = 2.1…
- Moist air at 40 °C and 60% relative humidity (saturation pressure 7.384 kPa) is at 101.325 kPa. Its humidity ratio is
- Moist air at 20 °C and 40% relative humidity (saturation pressure 2.339 kPa) is at 101.325 kPa. Its humidity ratio is
- A room's cooling load has 30 kW sensible and 15 kW latent components. The sensible heat factor is
- A room's cooling load has 20 kW sensible and 8 kW latent components. The sensible heat factor is