Mechanical EngineeringVery hard
A refrigerator working between an evaporator at -10 °C and a condenser at 30 °C has an actual COP of 3. Its COP relative to the Carnot COP is
- A. 19.7 %
- B. 57.0 %
- C. 45.6 %
- D. 39.6 %
Correct answer: C. 45.6 %
Carnot COP = Te/(Tc − Te) = 263/40 = 6.58; relative COP = 3/6.58 = 45.6%.
Practise more Heat Transfer, Refrigeration & Air Conditioning (Mechanical) questionsHeat Transfer, Refrigeration & Air Conditioning (Mechanical): notes and key points
More Heat Transfer, Refrigeration & Air Conditioning (Mechanical) questions
- An ideal reversed Brayton (Bell–Coleman) air refrigerator operates at a pressure ratio of 3 with γ = 1.4. Its COP is
- An ideal reversed Brayton (Bell–Coleman) air refrigerator operates at a pressure ratio of 4 with γ = 1.4. Its COP is
- In a Bell–Coleman cycle air leaves the cold space at -10 °C and, after compression to a pressure ratio of 5 and cooling, enters the…
- A plant makes 10 tonnes of ice per day from water at 30 °C, the ice leaving at −8 °C (cpw = 4.18, latent heat 335 kJ/kg, cp,ice = 2.1…
- A plant makes 15 tonnes of ice per day from water at 30 °C, the ice leaving at −5 °C (cpw = 4.18, latent heat 335 kJ/kg, cp,ice = 2.1…
- Moist air at 40 °C and 60% relative humidity (saturation pressure 7.384 kPa) is at 101.325 kPa. Its humidity ratio is