Electrical EngineeringVery hard
A 100 kVA transformer with iron loss 1000 W and full-load copper loss 3200 W delivers load at 0.9 pf. Its maximum efficiency is
- A. 98.05 %
- B. 95.54 %
- C. 94.75 %
- D. 96.18 %
Correct answer: D. 96.18 %
x = √(Pi/Pc) = 0.559; output = 50.31 kW; total loss = 2Pi = 2000 W; ηmax = 96.18 %.