Electrical EngineeringVery hard
A 500 kVA transformer with iron loss 1000 W and full-load copper loss 6000 W delivers load at 1 pf. Its maximum efficiency is
- A. 99.51 %
- B. 99.03 %
- C. 98.62 %
- D. 98.34 %
Correct answer: B. 99.03 %
x = √(Pi/Pc) = 0.408; output = 204.12 kW; total loss = 2Pi = 2000 W; ηmax = 99.03 %.